I have an AB MAB series CIP safety gate. When I close the door, it is supposed to detect the lock module but, it doesnt. Can anybody help me?
top of page



Welcome to Common Automation
Common Automation is a platform to share your engineering knowledge, stories and tip&tricks. Share your valuable knowledge here to help fellow engineers.
bottom of page
Hello Andy, it looks like your lock module is not paired with the CIP module. To meet SIL 3 safety requirement, the lock module has RFID pairing with the CIP module. Reset the module from your "Device properties" tab in studio 5000. If its still not working, probably somethings wrong physically.